Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

Control Transformer for DDC control

Status
Not open for further replies.

techzone12

Mechanical
May 9, 2005
31
0
0
US
We are installing VAV controllers in the ceiling plenum of a building. The controllers require 24V and each one is 10 VA rated.

How big of a 24V transformer can we install in the ceiling plenum to provide power to the controllers? What are the limitations by the NEC code? If the controllers, as an example, going to draw 5 amps total, is this allowed by the code?

Thanks
 
Replies continue below

Recommended for you

be careful... i think that would be a class 2 transformer, (it's been a while since i last checked code on this)... but the largest acceptable transformer for DDC controls in an environmental air plenun is 96va. If i can find the manufacturer and part number, i will post it. I originally put 200va transformers in for DDC controls and the local AHJ quickly corrected me. The solution and what the AHJ approved was a 96va transformer.
 
Status
Not open for further replies.
Back
Top