By now you may be armed with the offshore reliability data. You also state that your issue is with manufacturing. Consider other perspectives.
Predetermined failure position.
In the control system business we address the topic of control valve failure as it relates to the spring action. Engineers determine the prefereed failure mode. Usurally we want the steam valve that provides energy to a chemical reactor to fail closed. Perhaps we want the cooling water to the same reactor to fail open. These are actuated valves that typically use a spring-opposed diaphragm or piston to move the valve. Upon loss of the actuating supply medium such as air or hydraulic pressure, the spring moves the valve to the predetermined safe location. In these actuated valves the term failure can be interpreted as loss of the actuating medium. Besides failure of the air compressor system, wet dirty air is a common cause of air supply problems. In cold climates por quality air can freeze.
Valve trim problems are often a function of the misapplication of the valve more than a manufacturing issue. Water can wire-draw the plug and seat of a control valve plug when it operates very near the seat. This can occur with some of the hardest trim materials. The controls can be applied to avoid operation with the plug near the seat. Many misapplication issues exist. Some valves intended for open/closed operation may be used to throttle. Misapplication is a far greater problem for control valves than manufacturing.
Bubble-tight shutoff valves work great in the lab. However, just the rust and dirt contained in hydrostatic testing fluids can scratch the seating surface for a ball-valve in a manner that causes some leakage.
The list of valve failure issues can go on forever. What issues are of interest in your question?
John