friartuck
Mechanical
- May 31, 2004
- 402
Hi Folks
I need some help on how to control the AHU in a clean room system.
I have constant volume regulators on the terminal HEPA filter boxes which are designed to hold a constant flow rate regardless of the supply system pressure. But heres the BUT...
I would like to control the AHU with a velocity probe and Inverter (VSD) to the fan motor.(to save energy)
My question is, that the controls will in effect be 'open loop.' and there will be a conflict between the inverter control and the CV boxes.
How do I set up the controls? If I set the AHU to perform a constant velocity, what stops the CV regulators from going wild and closing if the airflow from the AHU is a tad too high.
Am i better setting the inverter VSD drive to control from a set supply duct static pressure rather than a set velocity. That way, the CV's will adjust to the main duct pressure.
What I would like to do is save energy by having the fan ramp up gently as the HEPA filters get dirty.By doing a simple set supply duct pressure control, i won't achieve that.
I have considered monitoring the terminal HEPAS and setting the supply duct pressure such that it will adjust in steps according to the highest terminal filter pressure drop. i.e if I monitor 5 terminal hepas, if the fan supply pressure is set initially at say 400Pa, i can adjust its set point in step with the hepa filter incresae. So if the hepa PD goes up by 100pa, I simply increase the control point by another 100Pa to give me 500Pa at the supply fan outlet.
Any suggestions
Friar Tuck of Sherwood
I need some help on how to control the AHU in a clean room system.
I have constant volume regulators on the terminal HEPA filter boxes which are designed to hold a constant flow rate regardless of the supply system pressure. But heres the BUT...
I would like to control the AHU with a velocity probe and Inverter (VSD) to the fan motor.(to save energy)
My question is, that the controls will in effect be 'open loop.' and there will be a conflict between the inverter control and the CV boxes.
How do I set up the controls? If I set the AHU to perform a constant velocity, what stops the CV regulators from going wild and closing if the airflow from the AHU is a tad too high.
Am i better setting the inverter VSD drive to control from a set supply duct static pressure rather than a set velocity. That way, the CV's will adjust to the main duct pressure.
What I would like to do is save energy by having the fan ramp up gently as the HEPA filters get dirty.By doing a simple set supply duct pressure control, i won't achieve that.
I have considered monitoring the terminal HEPAS and setting the supply duct pressure such that it will adjust in steps according to the highest terminal filter pressure drop. i.e if I monitor 5 terminal hepas, if the fan supply pressure is set initially at say 400Pa, i can adjust its set point in step with the hepa filter incresae. So if the hepa PD goes up by 100pa, I simply increase the control point by another 100Pa to give me 500Pa at the supply fan outlet.
Any suggestions
Friar Tuck of Sherwood