subash148
Electrical
- Aug 22, 2014
- 20
I have a GSU transformer with the following rating and would like to know if I am given a single phase no load and load losses or three phase no load and load losses, how to convert these losses between single phase and three phase GSU transformer and vice versa. I am in the process of selecting a vendor for a GSU transformer bid.
Here is the rating of GSU transformer:
MVA Rating: 54/72/90 MVA
Class Type: ONAN/ONAF/OFAF
Primary Voltage Rating: 13.8 kV
Secondary Voltage Rating: 242 kV
The transformer is single phase with Delta-Primary and Wye-grounded-secondary. These three single phase transformers will be connected in parallel to make a three phase step up transformers.
Here is a two different values with the load losses and no load losses given by two different bidders(vendor) for single phase and three phase GSU transformer respectively:
Bidder-A:90 MVA- Single Phase Unit
No Load Losses= 41.5 kW
Load Losses= 187 kW
Bidder-B:270 MVA- Three Phase Unit
No Load Losses= 84 kW
Load Losses= 889.5 kW
Based on the above scenario, please let me know how to convert single phase losses to three phase losses and three phase losses to single phase losses?
Thank you for your help in advance.
SG