I have a question concerning utilizing ventilation to cool an electrical room.
The electrical room has 2 transformers that are generating 100,000 btu/hr of heat. I would like to provide ventilation to the space to handle this load. The summer design day temp is 94 degrees.
If I were to calculate the room temperature to be 100 degrees, then I would need 15,432 CFM to maintain that temp. That is a tremendous amount of air for a space that is 2000 ft3.
My question is what is the maximum ACH limit for an electric room where the air is being removed so quickly that the temperature rise from the transformers is not actually increasing the temp of the room and the room temp is ambient temp. At 15,432 CFM, the ACH rate is 463 and it will feel like a jet engine going off in that room.
Michael
The electrical room has 2 transformers that are generating 100,000 btu/hr of heat. I would like to provide ventilation to the space to handle this load. The summer design day temp is 94 degrees.
If I were to calculate the room temperature to be 100 degrees, then I would need 15,432 CFM to maintain that temp. That is a tremendous amount of air for a space that is 2000 ft3.
My question is what is the maximum ACH limit for an electric room where the air is being removed so quickly that the temperature rise from the transformers is not actually increasing the temp of the room and the room temp is ambient temp. At 15,432 CFM, the ACH rate is 463 and it will feel like a jet engine going off in that room.