A HVAC system for conditioning of a clean manufacturing area includes a cooling system for mixed air preparation. This cooling system is used for supplied air dehumidification too. The required humidity that is set up for the manufacturing clean area is more than 35% (lower limit) and due the environmental reasons not more than 55% (upper limit).
The cooling system utilizes a two stages 40 ton (2x 20 ton compressors) condensing unit connected with refrigerant piping to two face split cooling coils in an air handling outdoor unit for mixed air preparation. All of the operations are controlled through a DDC control system.
At low loads of required refrigeration and at temperature below 50° F in the dehumidification stage, the coils are frizzing and the ice is closing 2/3 of the air pass trough surface, causing a general malfunction of the whole system. The low load control of the DX coils system seems to be through compressor unloading and hot bypass.
If you have some ideas about how this problem can be solved, please advice. A water/glycol chiller as a controlled cold source might help?
Thanks
The cooling system utilizes a two stages 40 ton (2x 20 ton compressors) condensing unit connected with refrigerant piping to two face split cooling coils in an air handling outdoor unit for mixed air preparation. All of the operations are controlled through a DDC control system.
At low loads of required refrigeration and at temperature below 50° F in the dehumidification stage, the coils are frizzing and the ice is closing 2/3 of the air pass trough surface, causing a general malfunction of the whole system. The low load control of the DX coils system seems to be through compressor unloading and hot bypass.
If you have some ideas about how this problem can be solved, please advice. A water/glycol chiller as a controlled cold source might help?