Currently commissioning a compressor skid, however having trouble with the motor running the cooling fan.
Basically the motor is rated for 15kw / 33.7amps OPERATING BETWEEN 380 - 415v however during the test the amp reading is 36amps. Have reduced the angle of the blades to reduce the effort and its now down to 14.3kw but still pulling 36amps. I was told by the lead electrical test to change the ABB overload to a higher rating, but I feel this only masks the problem as the problem seems to lie within the motor set up.
Any ideas or experience of similar, I am wandering if it could be a waiting issue.
Many Thanks,
B
Basically the motor is rated for 15kw / 33.7amps OPERATING BETWEEN 380 - 415v however during the test the amp reading is 36amps. Have reduced the angle of the blades to reduce the effort and its now down to 14.3kw but still pulling 36amps. I was told by the lead electrical test to change the ABB overload to a higher rating, but I feel this only masks the problem as the problem seems to lie within the motor set up.