moideen
Mechanical
- May 9, 2006
- 359
I have a cooling tower; capacity mentioned in submittal that 450 ton. Centrifugal chiller capacity is 450 ton. Very clear cooling tower is undersized. In the summer running two towers for one chiller. As per the same document, the condenser flow rate is 1350 gpm and range 10F. Then capacity will be 1350*500*10=562 ton. I don’t know what happened in design and selection time. I am planning to increase the capacity and improve the efficiency of chiller. Stiil I have a confusion, why the design eng selected 1350 gpm for 450-ton chiller