francis_mechanical,
You are in right path.
1. You have to find out what is cooling water requirements for each engine. This give you water flow, inlet and outlet temperature ranges. By multiplying by 26 you have got total cooling water flow, which is you calculated to be 2,600 gpm, I assume. We probably will have constant flow closed circuit cooling water system.
2. From Crane reference table I can find out that for 2500 gpm: 7.17 fps for 12" X SCH40, and 5.93 fps for 14" X SCH40. I think, for this type of application 12" pipe is minimum you can use. Please note that 12" pipe STD (0.375") and SCH40 (0.406") doesn't much, so be careful! Corrosion Allowance for this type of application will be around 1/16"-1/8".
3. So you probably will have 5 psi pressure drop across each engine (please check this number from engine manufacturer), so you will have about 10-15 psi differential pressure between supply and return headers. You will have another 10 psi allowance for your Air Cooler (I think you can use Air Cooler to cool water), and 10 psi pressure drop through all piping. So we will need 35 psi total DP for your pump. Probably three (3) pumps at 50% flow is a good idea as mentioned above (two pumps running, one stand-by), so your pump shall be able to deliver 1300 gpm @ 35 psi. Your system will have 50 psig design @ 100C. Piping will be uninsulated (except areas where human can hurt themselves by touching high temp surface).
4. You will have supply and return header 12"xSTD and 26 branches going to and coming from engines. For 88 gpm flow for each engine 2" pipe may be sufficient (Crane says 8.6 fps for 90 gpm). I think you can use STD wall pipe, but many specs use "extra strong" XS wall for small bore piping 2" and below for corrosion allowance.
5. I recommend to use manual butterfly valves to adjust flow on each branch going to each engine. These come flangeless body and installed between two flanges. During start-up these will be adjusted to have 88 gpm through them and locked. It is simple and not expensive solution for constant flow application. Of course you can install control valves with flow meters on each line and control flow through it (I don't think it will add any value, except cost).
6. You will have in the end supply and return header 3"-4" by-pass line with by-pass valve. This line needed to control differential pressure between supply and return header, and will be helpful during start-up and adjusting flows to each of 26 engines.
7.Now, you can size Air Cooler, based on supply and return temperature ranges, we can determine how big cooler do you need. Use summer hottest air temperature for Air Cooler sizing. 10 psi pressure drop should be maximum, but do not go below 4 psi because you may have problem with flow distribution. I think stainless steel tubes with extruded AL fins are most cost efficient Air Cooler designs. You can choose from number of suppliers who can built and supply complete package with fans.
8. Once you have sizing of Air Cooler, and preliminary layout, you can calculate internal volume of your system. You need this to calculate an expansion tank, because your system is closed system, and you need a space for expanding volume of water. So you will need an expansion tank, which should have internal volume of 200% - 300% of volume calculated expansion volume of water. You expansion tank will be installed close to suction side of the pumps.
9. If you have gone this far, now you can draw P&ID of the system, have Line List, Equipment List, Valve List, PRV List (you will need at least two, one for Air Cooler, one for Expansion Tank), Instrument List (Pressure and Temperature gauges), and start cost estimate of the system.
10. Anything else? You can try to get built a Pump Skid and install all three pumps in a steel skid with all piping, instrumentation, valves, expansion joints. This will reduce site costs, because all of this can be built at fabrication shop for a fraction of the cost of the on site costs. Of course you have to have a space to bring in this skid into you location. You have to have close attention to structural and foundation design for this pump skid because of vibration issues you may have. You may consider using glycol, if you need freeze protection in case you system will be down (emergency, maintenance, whatever reason) in winter. Please keep in mind there is slight difference between properties of water and glycol-water solution.
Regards,
Curtis