I have question about the protective device coordination for arc flash study. We have a generator, then a high voltage circuit breaker interlocked with 50/51/51N relays, then 13.8/4.16kV transformer, then a high voltage circuit breaker interlocked with 50/51/51N relays, and then the switchgear.
My question is that while performing the coordination study, should I plot the TCC (time current curves) for only the relays, or for relays as well as breakers?
As the relays are already interlocked to breakers, so it makes sense to plot the TCC curves for only the relays and not for the breakers. But also there is an instantaneous element of the breakers and it might be required to plot the TCC for instantaneous element of breakers along with the TCC of the relays on the same log-log paper.
My question is that while performing the coordination study, should I plot the TCC (time current curves) for only the relays, or for relays as well as breakers?
As the relays are already interlocked to breakers, so it makes sense to plot the TCC curves for only the relays and not for the breakers. But also there is an instantaneous element of the breakers and it might be required to plot the TCC for instantaneous element of breakers along with the TCC of the relays on the same log-log paper.