Copper in dry pipe system??

Status
Not open for further replies.

TravisMack

Mechanical
Sep 15, 2003
1,757
I have a consultant that is requiring a dry system for an MRI room. Typically, we do wet pipe CPVC or Copper in MRI rooms. However, since this is a dry system, CPVC is out. Is there anything prohibiting Copper tubing in a dry system? Would I still use a C-150 for the calcs if it is permissible?

Thanks in advance for any help.

Travis Mack
MFP Design, LLC
 
Replies continue below

Recommended for you

do not have the book, but I think it is allowed
 
I found the information. Thanks. It is allowed. You have to braze the copper and not solder. Other than that, no real problems.

I have just never encountered a dry pipe system using copper piping.

Travis Mack
MFP Design, LLC
 
"I have just never encountered a dry pipe system using copper piping."

When you go to purchase the copper you'll know why.

But we do learn something new every day. Thanks.
 