Does anyone have a good reference on how placement of conductors within a Core Balance (Zero Sequence) CT can affect the accuracy?
We had a situation where a 480V motor failed. The 480V system is fed from a 7200 V system through a Dyn1 transformer. The feed to the transformer passes through a 50:5 CBCT with a 50G set at 2A (20A primary). A solid ground fault on the 480V side puts about 1500A on two of the 7200V side phases. If badly placed in the CBCT, could we get 2A of error current and the trip, or do I need to expand my search?
We had a situation where a 480V motor failed. The 480V system is fed from a 7200 V system through a Dyn1 transformer. The feed to the transformer passes through a 50:5 CBCT with a 50G set at 2A (20A primary). A solid ground fault on the 480V side puts about 1500A on two of the 7200V side phases. If badly placed in the CBCT, could we get 2A of error current and the trip, or do I need to expand my search?