ixv

Structural
Nov 8, 2018
16
0
0
MT
What are the main concrete core checks one has to calculate in a multistorey building ?
 
Replies continue below

Recommended for you

I don't follow your question. Are you talking designing a reinforced concrete core (like a elevator shaft) in a building? Taking core samples to evaluate a existing building? Need more details.
 
I am referring to a concrete core that is for ventilation and elevator shafts and fire escape stairways. It is main to be the a form of stability system for the high rise.

I have calculated the axial loading and the wind loading which is a point load at every storey and have used the h/300 equation for the deflection.

I have read that a method called the Area Moment Method has to be used but I am not sure how exactly I will arrive to the solution that the concrete core is stable enough. This core is 14m*14m* placed in the middle of a circular 20 storey high rise with 2 basement garages underneath.
 
Please tell me what building this is so I can make sure I don't go in it.

Moment area method is not a stability analysis, it's a design method for calculating slope and deflection in beams of varying cross section. Wind loading is not a "point load at each story", there are torsional forces and other design considerations. If you don't know these you should have no business designing the lateral-force resisting system of a 22 story, high-rise structure!

Ian Riley, PE, SE
Professional Engineer (ME, NH, VT, CT, MA) Structural Engineer (IL)
American Concrete Industries
 
I feel your pain here. In my opinion shaft design is one of the most complex problems in structural engineer and, simultaneously, a problem that gets almost no treatment in mainstream textbooks. The problem seems to be getting exacerbated by our reliance on FEM software as well. With such "accurate" tools available to us, we seem to be losing our motivation to truly understand this stuff. Fundamentally, a core is just a cantilevered beam with a bunch of holes in it. It's astounding how complex that makes the problem however. Some excellent resources that I've drawn from are shown below. A very non-exhaustive list of things that may need to be checked includes:

1) Drift
2) Flexural strength.
3) Shear strength.
4) Torsional strength.
5) Force transfer around openings.
6) Coupling beam capacity and behavior.
7) Dynamic characteristics under wind and their influence on occupant comfort.
8) Ductile detailing in high seismic designs.
9) Potential for seismic pounding against adjacent structures.
10) Global stability in the transnational sense.
11) Global stability in the torsional sense (tall + single core)
12) Differential shortening between shaft and columns for tall buildings and, particularly, those with outriggers.
13) Shear transfer across floor level cold joints if those exist.
14) Overall axial capacity.
15) Backstay effects where basements are involved.
16) Behavior and detailing at transfer diaphragm levels where concentrated load is moving from one wall group to another.
17) Compression stability of wall ends.
18) Appropriate flange widths for both tension and compression flanges of wall groups.
19) Shear friction along the vertical joints between interconnected segments of wall groups.
20) Anchorage -- not just development -- of core vertical bars into foundation elements.

Obviously, not all of these things are germane to all building morphologies. It's a much simpler problem for modest structures.

I have all of the references below in my library. If you plan to do some shopping, I can elaborate on the strengths of each. I'll only respond to targeted questions however. I don't have time to write book reports on all this stuff for sport.

c01_s4rpk3.jpg

c02_wgmup2.jpg

c03_xmecvs.jpg

c04_mzebny.jpg

c05_dtqxdb.jpg

c06_eepem7.jpg
 
To paraphrase a conversation I had with Koot elsewhere. "Tall buildings are actually easier than short buildings. There's a well defined load path out of necessity. A 15 storey building is no harder than a 5 storey. It's just more storeys."
 
Status
Not open for further replies.
Back
Top