Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Coring Elevated Concrete Floor Deck 2

Status
Not open for further replies.

vmirat80

Structural
Nov 9, 2020
7
Contractor wants to drill 4-inch diameter holes through a second floor concrete/metal pan deck for conduit. Deck span between floor beams is about 8 feet. At what point do these holes compromise the strength of the deck?
 
Replies continue below

Recommended for you

If you miss the rebar, a hole this size has no effect. Even if you hit the rebar, it will have little effect unless the floor is highly loaded.

 
KootK, thanks for the docs, very helpful! Unfortunately, they still leave a lot to be figured out.
- If there are four 4-inch holes running perpendicular to the deck flutes, how far apart can they be from each other so that they don't count as one big opening? My guess, based on their rules of thumb, is that if the holes are spaced so that there is at least 12 inches of deck between them, then they are considered individual holes, assuming the holes are 6-inch diameter or less.
- It seems these documents are written with the assumption that the deck is a composite construction (concrete and metal pan acting together). The floor deck I'm dealing with is not.
- I tried to get the SDI white paper "Deck Damage and Penetrations" but their web site says it's been withdrawn.
 
So the steel deck is just formwork? Then it would be up to you to analyze it the same as a concrete slab without the deck. Can they accurately miss teh reinforcing? If so, I don't expect it to be much of a problem from a flexural perspective. It would be up to you to see if it has implications for the shear capacity of the slab.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor