powering2002
Electrical
- May 8, 2008
- 33
Dear all,
Last week Our Boiler Feed Pump Motor was tripped few seconds after started. From The Event Recorder in The Relay Panel, it was found that the cause was Short Circuit Trip.The current at that time were 1506 A (Phase A),1125 (Phase B), and 1115 (Phase C) . It exceeded the Short Circuit Instantaneous Setting value, which is 1500 A. So, we checked the motor. We performed PI test and megger Test. The Insulation Resistance was Good. It exceeded 4 MegaOhm. The PI value was 5,54. Then we started the motor again. and it ran well. My question are:
1. Is our instantanous short circuit trip setting was correct?
2. Is this high starting current caused by DC offset?
3. Does we need to increase the instantanous short circuit trip setting to avoid this false tripping?
Thanks for your attention.
Note: here is the specification of our BFP motor:
KW : 950
AMPERE : 161
VOLT : 4000
RATING : CONT.
STARTING : FULL VOLT
FORM : VCCN
HZ : 50
RPM : 2960
AMBIENT TEMP : 40° C
POLE : 2
STATOR INSULATION CLASS : B
STANDARD SPECIFICATION : JEC 37
Last week Our Boiler Feed Pump Motor was tripped few seconds after started. From The Event Recorder in The Relay Panel, it was found that the cause was Short Circuit Trip.The current at that time were 1506 A (Phase A),1125 (Phase B), and 1115 (Phase C) . It exceeded the Short Circuit Instantaneous Setting value, which is 1500 A. So, we checked the motor. We performed PI test and megger Test. The Insulation Resistance was Good. It exceeded 4 MegaOhm. The PI value was 5,54. Then we started the motor again. and it ran well. My question are:
1. Is our instantanous short circuit trip setting was correct?
2. Is this high starting current caused by DC offset?
3. Does we need to increase the instantanous short circuit trip setting to avoid this false tripping?
Thanks for your attention.
Note: here is the specification of our BFP motor:
KW : 950
AMPERE : 161
VOLT : 4000
RATING : CONT.
STARTING : FULL VOLT
FORM : VCCN
HZ : 50
RPM : 2960
AMBIENT TEMP : 40° C
POLE : 2
STATOR INSULATION CLASS : B
STANDARD SPECIFICATION : JEC 37