To Bill's point on the lower size limitation based on allowable voltage drop, if the generator is feeding only that one motor, and you have dealt with control power loss issues, sometimes people allow the generator voltage to drop and bring the motor up to speed with the engine by letting the generator slow down. The trickery part is that left alone, your control system will shut down when you do that. So either you have a control system tht can take a very wide input range, or you have a UPS on it.
In general though, if you need to accelerate a 16MW motor from an 18MW generator capacity system, the only way that can possibly happen is by having a VFD of some sort on the motor, even if you do not need to vary the speed when running.