CN-EIT
Structural
- Feb 10, 2020
- 31
For starters, I have referenced this prior thread Link.
Existing design criteria:
1) Ex. 21WF62 A36 Steel Beam.
2) Beam is 18'-0" long simple span with standard shear connections to supporting girders.
3) Beam is non-composite and carries a 4" thick concrete slab.
4) Design loads are DL=25psf (superimposed) & LL=200psf (industrial use)
Context: Beam supports industrial equipment. Originally, the center third of the beam supported equipment which produced a liquid that corroded the beam. The end thirds of the beam did not have equipment but are also corroded.
Corrosion summary:
1) Center Third-
2) End Thirds-
The concrete floor has only been removed over the center third. The area does not currently have design surface loads or equipment, only the concrete slab. There are 10 of these beams in total. Given we are halfway through the plant scheduled shutdown, schedule is a concern and as such repairs, not replacement of, of the beams is desired.
The attached is a sketch of what I have in mind, basically plating the entire beam. Where we have near total loss of structural cross section at the center third, the plates would need to take the entirety of the load; essentially a 6'-0" long splice that needs to develop the forces back into the end thirds of the beams which would carry it to the existing connections (ex. connections are not corroded). Before we go down the "just replace the beams" line, there are substantial impacts to surrounding area trying to replace these beams, that is a last resort in this instance.
What I am looking for:
1) General thoughts and concerns on the detail.
2) Required surface prep to actually accomplish sound welds.
Existing design criteria:
1) Ex. 21WF62 A36 Steel Beam.
2) Beam is 18'-0" long simple span with standard shear connections to supporting girders.
3) Beam is non-composite and carries a 4" thick concrete slab.
4) Design loads are DL=25psf (superimposed) & LL=200psf (industrial use)
Context: Beam supports industrial equipment. Originally, the center third of the beam supported equipment which produced a liquid that corroded the beam. The end thirds of the beam did not have equipment but are also corroded.
Corrosion summary:
1) Center Third-
-Web: uniform pitting corrosion ranging from 1/16" to 1/8" material loss each side of web
-Top Flange: loss of flange thickness & width from 3/8" to entire flange thickness and 50" reduction in flange width: top of flange was visible.
-Btm Flange: Consistent and uniform pitting from 1/8" to 3/16" material loss on top & bottom surface of flange
Top surface of btm flange shows portions of delamination from the edge of flange into the fillet (k) region of the beam
-Web/Flange: localized portions of steel delamination
2) End Thirds-
-Web: uniform and consistent pitting corrosion ranging from 1/16" to 1/8" material loss each side of web
-Top Flange: uniform and consistent pitting corrosion ranging from 1/16" to 1/8" material loss bottom side of flange, top side of flange not visible, though flaky material was able to be chipped away at locations where concrete slab had not entirely concealed edge of flange. Flaky material appeared consistent with portions of exposed flange at center third where delamination/corrosion was observed.
-Btm Flange: Consistent and uniform pitting from 1/8" to 3/16" material loss on top & bottom surface of flange.
The concrete floor has only been removed over the center third. The area does not currently have design surface loads or equipment, only the concrete slab. There are 10 of these beams in total. Given we are halfway through the plant scheduled shutdown, schedule is a concern and as such repairs, not replacement of, of the beams is desired.
The attached is a sketch of what I have in mind, basically plating the entire beam. Where we have near total loss of structural cross section at the center third, the plates would need to take the entirety of the load; essentially a 6'-0" long splice that needs to develop the forces back into the end thirds of the beams which would carry it to the existing connections (ex. connections are not corroded). Before we go down the "just replace the beams" line, there are substantial impacts to surrounding area trying to replace these beams, that is a last resort in this instance.
What I am looking for:
1) General thoughts and concerns on the detail.
2) Required surface prep to actually accomplish sound welds.
My thought is, to actually develop the forces out of those plates and into the end third of those existing beams, they would need to grind down all of the pitting corrosion down to a smooth steel surface. There is foreign material (source of corrosion) sitting on those flanges, chipping it away showed that the steel was moist/wet under it, in addition to the grinding, would these beams need to "dry out" prior to welding to prevent continued corrosion?
3) Shear flow, and where to start with that. Resources on that are welcome.