GMcD...I totally agree with you. I am in the Testing, Adjusting, and Balancing field. The largest hurdle I have to overcome when working on a hydronic balancing project is AIR in the system. There is nothing worse, in my opinion. An Airtrol (depending on what type of Airtrol)will take the dissolved air out of a system at or near the pumps, and air bleeders installed at the lowest point of solubility (generally the highest point of the system) will take the air out at that point. I have yet to see an enclosed hydronic system where air is a helpful factor.
SO...Bleed air, fill with liquid, repeat until ALL of the air is out of a system. Keep in mind that a lot of air bleeders installed at the high point WILL let air IN to the system if it is not 100% full. Shoot for about 10 psi at the high point. Sometimes, perhaps on a shutdown or something similar, it seems that air will find it's way to the high point, rather than being entrained "midstream"...so my point is, it may be helpful to shut a system off and wait for air to bleed out.
I apologize for the lenghty reply, I am sure there is a thread on this topic somewhere else...