CPVC hangers

Status
Not open for further replies.

fpst

Computer
Jan 20, 2012
109
For CPVC piping, in NFPA 13 2013 which allows cumulative sprinkler hanger distances, I can't find a maximum unsupported length.

"9.2.3.2.5* A single section of pipe shall not require a hanger when the cumulative distance
between hangers on the branch line does not exceed the spacing required by Table 9.2.2.1(a)
and Table 9.2.2.1(b)."

In the blazemaster listing (for example) I see a section about vertical support of sprinkler piping - the vertical support can be on two sides of every sprinkler/sprinkler drop or directly before a sprinkler/sprinkler drop. The dimensions given for "one support" is 1'-0 for 1" CPVC, for example.

I'm trying to determine three things:

1. Can this "vertical support", if it's something like a standoff hanger, be counted as a support not only against upward thrust, but also as a pipe hanger (keeping it suspended when sprinkler is not active) itself. I suspect the answer is yes so my next questions are:

2. If you have a 1" blazemaster CPVC pipe going to a sprinkler, what is the maximum distance the centerline of the sprinkler can be from the nearest hanger.

3. Can the hanger be on the CPVC cross main?

I've read the listing/NFPA 13 2013, just want to verify I'm interpreting it right.
 
Replies continue below

Recommended for you

After more research it appears 1. yes if the listing says it can be used as a restraint and a hanger (some do)
2. 1'-0
3. Not unless the hanger on the cross main is less than 1'-0 (linear) from the sprinkler or sprinkler drop, assuming the arm over is 1" blazemaster.
 