EngDM
- Aug 10, 2021
- 588
I'm reviewing a spreadsheet from steeltools for slab on grades for use with CSA A23.3, and I came cross that the Mcr calculation according to 24.2.3.5 of ACI 318-19 is Mcr = fr*Ig/yt, CSA A23.3-14 shows the same equation, but stipulates that fr should be taken as half of the value calculated in equation 8.3 of A23.3.
I investigated the equations for fr to see if maybe ACI took the 1/2 in the equation, but no dice. This equation, for reference is 0.6λsqrt(fc') in CSA which is roughly equivalent to the 7.5λsqrt(fc') used in ACI with imperial units in equation 19.2.3.1 (in reality it is closer to using 7.2 instead of 7.5). Regardless, the 7.5>7.2 factor doesn't make up for the half.
P.S. the spreadsheet still shows a coefficient of 9 for MOR for those who use it, might be worth investigating whether changing it to 7.5 is appropriate.
Is anyone aware of why this is? I couldn't find if it was perhaps an ASD vs LSD design reason, but ACI 318 seems to be in LRFD which is comparable to how CSA does it (with phi factors).