alumpkin
Structural
- Sep 11, 2000
- 69
Gentlemen,
Please comment.
I have a 12 inch thick reinforced concrete slab on grade for a manufacturing plant in South Carolina. The reinforcment is #5@12" c/c each way top and bottom. The 3500 psi mix design is as follows:
cement 537 #
coarse agg (#57) 1046 #
coarse agg (#4) 400 #
Intermediate agg (#89) 696 #
Fine agg 1072#
Water 280#
W/C 0.52
Some mid range water reducer was used at the pour. This slab is on crusher run with no vapor barrier. Poures were approximately 10,000 sf. Diamond plates were used at the cold joints. Control joints were cut every 12'-6". Cuts were 1-1/2" deep which is just above the top reinforcing mat. All pours were interior pours and were covered. The curing compound/ hardener used was the Ashford Formula.
1
We have some random cracking in the slab but not a lot. The German side of the partnership is raising critical concern that our slab is suspect. Cracks are hairline and not structural.
Any thoughts concerning some random cracking for this slab? Why did the cracks not migrate to the saw cuts? As you can see the mix design is well graded mix chosen for its ability to reduce shrinkage and yet we still seem to have some random shrinkage cracking even with a 12'-6" pattern.
Please comment.
I have a 12 inch thick reinforced concrete slab on grade for a manufacturing plant in South Carolina. The reinforcment is #5@12" c/c each way top and bottom. The 3500 psi mix design is as follows:
cement 537 #
coarse agg (#57) 1046 #
coarse agg (#4) 400 #
Intermediate agg (#89) 696 #
Fine agg 1072#
Water 280#
W/C 0.52
Some mid range water reducer was used at the pour. This slab is on crusher run with no vapor barrier. Poures were approximately 10,000 sf. Diamond plates were used at the cold joints. Control joints were cut every 12'-6". Cuts were 1-1/2" deep which is just above the top reinforcing mat. All pours were interior pours and were covered. The curing compound/ hardener used was the Ashford Formula.
1
We have some random cracking in the slab but not a lot. The German side of the partnership is raising critical concern that our slab is suspect. Cracks are hairline and not structural.
Any thoughts concerning some random cracking for this slab? Why did the cracks not migrate to the saw cuts? As you can see the mix design is well graded mix chosen for its ability to reduce shrinkage and yet we still seem to have some random shrinkage cracking even with a 12'-6" pattern.