Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Criteria acceptance for Control Cables Continuity Test

Status
Not open for further replies.

Julinios

Chemical
May 14, 2007
6
Dear all:
For firefighting panel circuits our contractor is measuring 4 ohms for some cables.
Most of the cables have less than 1 ohm.
We are looking a norm to see the criteria acceptance.
Please advise if you have seen a similar issue.
Regards
 
Replies continue below

Recommended for you

Unfortunately there can be a lot of variation in what is acceptable. You'll hae to refer to a design standard for the panels. Typically when I see something like this it is an improper crimp terminal, with insulation stuck inside the crimp. Or it could be a wire with corrupted insulation that is rotting away slowly.

Z
 
How big is the deviation from the calculated value for the cables? Is it a measurement problem, or a cable which is installed properly but just longer than the others?
 
The Nationoal Electrical Code 2011 Chap 9 Table 8 Conductor Properties: 16 AWG, not stranding, copper and coated: 16.7 ohm/Km. The cable run is 60 m then we have 1.002 ohm but our measure is 4.1 ohms, the instrument calibration is ok, we are looking a "criteria acceptance" for "continuity check" to reject this circuits.
Thanks
 
How are you checking your 60m cable? Two hooked together for a loop so you can measure at one end? Could be a problem with your test connection. Can you confirm the high reading with a different return path/wire?

Are there other wires in the tray with the wires that are giving 4 ohm readings? Crosstalk may be corrupting your measurement. Maybe you could try an AC impedance measurement. Or a brute force test with a power supply and a current meter (1V/1A = 1 ohm, 1V/0.25A = 4 ohm). That may overcome any crosstalk, but may give a false positive if your panel circuits aren't as strong.

Have you tried other testers?

1.5 ohms seems like a very generous specification. Unfortunately you are failing that badly.

Z
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor