LJthien
Mechanical
- Jul 1, 2020
- 40
I have checked some related standards for this matter but still not get to know.
Our Solar Farm has operated for 6 months and we recently found that some Junction Boxes of PV modules (JB) had been bulged. We have investigated and pointed out the root cause that the connection of 1 of 2 JB cords was overheated at 110degC while the acceptable temperature is 85degC maximum as per IEC 62790(4.1).
In the result of the finding, there are 195 bulged JBs out of total 107.625 JBs. As the defect rate is 0.18%, I feel that the rate is not so high.
However, It must be convinced by a standard s' criteria to wrap up the non-conformity. Could you advise me which document I should refer to assess the defect rate of the defective JBs.
Thanks a lot.
Our Solar Farm has operated for 6 months and we recently found that some Junction Boxes of PV modules (JB) had been bulged. We have investigated and pointed out the root cause that the connection of 1 of 2 JB cords was overheated at 110degC while the acceptable temperature is 85degC maximum as per IEC 62790(4.1).
In the result of the finding, there are 195 bulged JBs out of total 107.625 JBs. As the defect rate is 0.18%, I feel that the rate is not so high.
However, It must be convinced by a standard s' criteria to wrap up the non-conformity. Could you advise me which document I should refer to assess the defect rate of the defective JBs.
Thanks a lot.