I have two scenarios here. First a description of the posts.
P1 - Single stud member with web at opening and capped with track. (1) 600S250-54 and (1) 600T200-54
P2 - Back to Back studs capped with track at opening. (2)600S250-54 and (1) 600T200-54
Height is 13'
Wind - 125 (gust 3)
Scenario 1 - The P1 jamb studs were installed with web side at opening and not capped. Sheathing has been put on and masonry veneer is nearing completion. Capping this is impossible without removing the sheathing (densglass and 1.6" HunterXci Plywood panels) and masonry. Are there means and methods for addressing this condition without removal of sheathing?
Proposed fix: Nest a 400S200-97 into 600S250-54 stud and cap the 4" member with track. See sketch attached.
Scenario 2 - Same parameters as above except P2 jambs have been installed as a box rather than an "I" and also without track.
Proposed Fix 1: Insert a 5x5x1/4" HSS column in between the boxed studs and secure this through the existing studs. Column to have no top or bottom plates.
Proposed Fix 2: Nest a 2x5x3/16" HSS column into the web of the stud closest to the window opening. This HSS would have an offset base-plate and anchored to the slab with 5/8" threaded rod with 6" epoxy embedment.
P1 - Single stud member with web at opening and capped with track. (1) 600S250-54 and (1) 600T200-54
P2 - Back to Back studs capped with track at opening. (2)600S250-54 and (1) 600T200-54
Height is 13'
Wind - 125 (gust 3)
Scenario 1 - The P1 jamb studs were installed with web side at opening and not capped. Sheathing has been put on and masonry veneer is nearing completion. Capping this is impossible without removing the sheathing (densglass and 1.6" HunterXci Plywood panels) and masonry. Are there means and methods for addressing this condition without removal of sheathing?
Proposed fix: Nest a 400S200-97 into 600S250-54 stud and cap the 4" member with track. See sketch attached.
Scenario 2 - Same parameters as above except P2 jambs have been installed as a box rather than an "I" and also without track.
Proposed Fix 1: Insert a 5x5x1/4" HSS column in between the boxed studs and secure this through the existing studs. Column to have no top or bottom plates.
Proposed Fix 2: Nest a 2x5x3/16" HSS column into the web of the stud closest to the window opening. This HSS would have an offset base-plate and anchored to the slab with 5/8" threaded rod with 6" epoxy embedment.