Hello Guys,
Recently join this community as I saw some really helpful posts. I've come across a control valve problem which has really high flow requirements.
The process conditions are as follows:
[ul]
[li]p1 = 10.3 barg[/li]
[li]p2 = 1 barg[/li]
[li]Q = 2,000,000 kg/hr[/li]
[li]k = 1.403[/li]
[li]M = 28.97 kg/kmol[/li]
[li]Z = 1 [/li]
[li]T = 65 degrees C[/li]
[/ul]
Based on k, the critical pressure ratio (p*/p0) is 0.5279. deltaP exceeds the critical pressure ratio therefore the fluid is supercritical and at sonic velocity.
The issue here is I believe the wrong valve has been selected which has an inlet diameter of 584mm and an outlet diameter of 510mm.
At the sonic velocity which is 369 m/s, the maximum flow rate possible (choked flow), should be limited to the flow rate possible through the 510mm restriction?
Using the equation:
Q = Cd * A * SQRT(k*rho0*P0*((2/k+1)^((k+1)/(k-1))))
Q = Flow rate (m^3/s)
Cd = discharge coefficient (used 0.9)
A = area (m^2)
k = specific heat ratio
rho0 = density at temperature, pressure and compressibility (kg/m^3)
P0 = inlet pressure (Pa)
I calculate this to be approx 1,570,000 kg/hr which is less than the flow rate required however at 584mm its approx 2,050,000 kg/hr?
If this is correct,the best option here would be to increase the size of the outlet to 584mm also?
Furthermore, I calculated the velocity at the outlet if the flow rate is 2,000,000 kg//hr:
Q = 2,000,000 kg/hr
A = 0.292 m^2 (using outlet diameter of 609.6)
rho2 = 2.07kg/m^3 assuming T2 = T1
This gave me a really high outlet velocity of 919.55 m/s. The valve outlet is attached to an expander which increase to 56".
Will this velocity be achievable on the outlet? Or will it be limited to M = 1 i.e. 369m/s?
Furthermore, if the velocity at the valve exit is M=1, will the expander continue to increase the velocity? (Following the principle of De Laval nozzle where outlet velocity can exceed M=1) or will it be subjected to Fanno flow?
Also, considering deltaP exceed critical pressure, what would the pressure at the valve outlet be? Would it be 5.43737 barg and then this down to 1 barg at the outlet of the pipe?
If any clarification is needed, please ask.
Recently join this community as I saw some really helpful posts. I've come across a control valve problem which has really high flow requirements.
The process conditions are as follows:
[ul]
[li]p1 = 10.3 barg[/li]
[li]p2 = 1 barg[/li]
[li]Q = 2,000,000 kg/hr[/li]
[li]k = 1.403[/li]
[li]M = 28.97 kg/kmol[/li]
[li]Z = 1 [/li]
[li]T = 65 degrees C[/li]
[/ul]
Based on k, the critical pressure ratio (p*/p0) is 0.5279. deltaP exceeds the critical pressure ratio therefore the fluid is supercritical and at sonic velocity.
The issue here is I believe the wrong valve has been selected which has an inlet diameter of 584mm and an outlet diameter of 510mm.
At the sonic velocity which is 369 m/s, the maximum flow rate possible (choked flow), should be limited to the flow rate possible through the 510mm restriction?
Using the equation:
Q = Cd * A * SQRT(k*rho0*P0*((2/k+1)^((k+1)/(k-1))))
Q = Flow rate (m^3/s)
Cd = discharge coefficient (used 0.9)
A = area (m^2)
k = specific heat ratio
rho0 = density at temperature, pressure and compressibility (kg/m^3)
P0 = inlet pressure (Pa)
I calculate this to be approx 1,570,000 kg/hr which is less than the flow rate required however at 584mm its approx 2,050,000 kg/hr?
If this is correct,the best option here would be to increase the size of the outlet to 584mm also?
Furthermore, I calculated the velocity at the outlet if the flow rate is 2,000,000 kg//hr:
Q = 2,000,000 kg/hr
A = 0.292 m^2 (using outlet diameter of 609.6)
rho2 = 2.07kg/m^3 assuming T2 = T1
This gave me a really high outlet velocity of 919.55 m/s. The valve outlet is attached to an expander which increase to 56".
Will this velocity be achievable on the outlet? Or will it be limited to M = 1 i.e. 369m/s?
Furthermore, if the velocity at the valve exit is M=1, will the expander continue to increase the velocity? (Following the principle of De Laval nozzle where outlet velocity can exceed M=1) or will it be subjected to Fanno flow?
Also, considering deltaP exceed critical pressure, what would the pressure at the valve outlet be? Would it be 5.43737 barg and then this down to 1 barg at the outlet of the pipe?
If any clarification is needed, please ask.