Hi,
We are performing a cross-bonding verification on a 220KV cable circuit with 11 joint bays.
The links and SVLs at all locations (termination link box and joint link boxes) have been placed in the normal service position.
At the far end of the cable, we have connected the three cable conductors together with heavy leads bolted to the cable terminations.
At the near end of the cable, we are injecting a 3-phase supply by way of a generator with the AVR bypassed - the generator exciter windings are energised by a manually controlled DC power supply, turning the generator into a constant current supply. We have done this test many times before and we are confident of the method.
The measured sheath currents are too high unless ALL the links are reversed.
i.e. at JB1, we measure 10A, which is too high. We reverse the links at JB1 to fault the cross bonding system and measure 30A, which is expected. If we then reverse the links at JB2 WITHOUT un-reversing the links at JB1 (i.e. so the sheath rotation is counter-clockwise rather than clockwise) the measured current drops to 0.5A.
This is the same for the remainder of the circuit.
My understanding is that the direction of rotation should not matter, as long as for each section, the 'contiguously connected sheath (if you see what I mean)' shares an equal distance with all three conductor phases.
Does anyone have any ideas?
We are performing a cross-bonding verification on a 220KV cable circuit with 11 joint bays.
The links and SVLs at all locations (termination link box and joint link boxes) have been placed in the normal service position.
At the far end of the cable, we have connected the three cable conductors together with heavy leads bolted to the cable terminations.
At the near end of the cable, we are injecting a 3-phase supply by way of a generator with the AVR bypassed - the generator exciter windings are energised by a manually controlled DC power supply, turning the generator into a constant current supply. We have done this test many times before and we are confident of the method.
The measured sheath currents are too high unless ALL the links are reversed.
i.e. at JB1, we measure 10A, which is too high. We reverse the links at JB1 to fault the cross bonding system and measure 30A, which is expected. If we then reverse the links at JB2 WITHOUT un-reversing the links at JB1 (i.e. so the sheath rotation is counter-clockwise rather than clockwise) the measured current drops to 0.5A.
This is the same for the remainder of the circuit.
My understanding is that the direction of rotation should not matter, as long as for each section, the 'contiguously connected sheath (if you see what I mean)' shares an equal distance with all three conductor phases.
Does anyone have any ideas?