WhiteyWhitey
Electrical
- Feb 3, 2009
- 61
Hiya,
I am commission a 275kV underground cable system.
System:
Conductor resistance is about 15m? per phase.
Each phase is a single core with Aluminium corrugated sheath cross bonded at the joint bays.
Background:
I am trying to test the cross bonding system. The goal being to prove using an onsite test that the cross bonding system is correctly connected and sufficiently cancels sheath currents.
The process I have been given is something like this:
1. Connect 3 phases of the remote end of the feeder together and to ground.
2. Connect a 3 phase 50A (thats Minimum, Preferably would like 100A) source to the feeder.
3. Inject 50A into the main conductor
4. At the joint bay record sheath induced curent and voltage on each sheath.
5. Reverse the cross bonding
6. Repeat measurement.
The theory is you should get current induced in the sheath of about 10A when correctly connected and this will be higher if the cross bonding is reversed (Say 30A)
Problem:
The machine I have is designed more for relay testing than current injection. The test set can produce 200A for 1 min when given a return current path (it has A phase output and A phase Common). When I maxed out the machine on the conductor I could only get it to produce 15A.
The measurements at the joint bay are too inaccurate and variable to be usable.
Question:
Does anyone have experience with this test?
What equipment should be used?
Is there a better way to test the cross bonding system?
Thanks in advance for your always Awesome tech advice.
Whitey.
I am commission a 275kV underground cable system.
System:
Conductor resistance is about 15m? per phase.
Each phase is a single core with Aluminium corrugated sheath cross bonded at the joint bays.
Background:
I am trying to test the cross bonding system. The goal being to prove using an onsite test that the cross bonding system is correctly connected and sufficiently cancels sheath currents.
The process I have been given is something like this:
1. Connect 3 phases of the remote end of the feeder together and to ground.
2. Connect a 3 phase 50A (thats Minimum, Preferably would like 100A) source to the feeder.
3. Inject 50A into the main conductor
4. At the joint bay record sheath induced curent and voltage on each sheath.
5. Reverse the cross bonding
6. Repeat measurement.
The theory is you should get current induced in the sheath of about 10A when correctly connected and this will be higher if the cross bonding is reversed (Say 30A)
Problem:
The machine I have is designed more for relay testing than current injection. The test set can produce 200A for 1 min when given a return current path (it has A phase output and A phase Common). When I maxed out the machine on the conductor I could only get it to produce 15A.
The measurements at the joint bay are too inaccurate and variable to be usable.
Question:
Does anyone have experience with this test?
What equipment should be used?
Is there a better way to test the cross bonding system?
Thanks in advance for your always Awesome tech advice.
Whitey.