Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations KootK on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Crosstie Requirement for Special Structural Walls

Status
Not open for further replies.

LearningAlways

Structural
Aug 17, 2014
68
When are these crossties required in a special structural precast wall?

Screenshot_2024-05-03_105359_um1dsm.png


We do not need special boundary elements; but we do need ties per ACI318-19 18.10.6.5. And so have created a 'non-special' boundary element.

The question is specific to the area outside of the boundary elements. Is there somewhere in the code that defines the need for them outside of the boundary element?

Screenshot_2024-05-03_105805_rk4udj.png
 
Replies continue below

Recommended for you

[quote
... The question is specific to the area outside of the boundary elements. Is there somewhere in the code that defines the need for them outside of the boundary element?][/quote]

Apparently the code is silent for the spacing of crossties outside of the boundary element .
Some points for the requirement and spacings of crossties
- The vertical reinf.should be restrained with crossties against buckling. In my zone, if the reinf. is wire mesh, the spacing of crossties max. 500 mm vertical and horizontal. If the longitudinal bar dia greater than 12 mm , spacing would be 20*D.

- NIST GCR 11-917-11REV-1 Seismic Design of Cast-in-Place Concrete Special Structural Walls .Suggests spacing max. 18 in. Copy and paste of the item ,
(...Verticals outside the boundary element provide required rl with spacing s ≤ 18 inches.)
...

He is like a man building a house, who dug deep and laid the foundation on the rock. And when the flood arose, the stream beat vehemently against that house, and could not shake it, for it was founded on the rock..

Luke 6:48

 
 https://files.engineering.com/getfile.aspx?folder=1c834723-7f16-4708-bf8d-870cce208050&file=nistgcr11-917-11_Seismic_Design_of_Cast-in-Place_wall___.pdf
Thank you for sharing that document HTURKAK. It is very helpful.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor