Recently when running an epoxy rebar anchor for tension in Hilti I came across a procedure in their design calcs that appear to be pretty ambiguos with the code. When calculating steel resistance of an anchor in tension, Hilti refers to equation D.2 which Nsar = Ase * phi[sub]s[/sub]*f[sub]uta[/sub]*R. The sentence below this in the annex D puts f[sub]uta[/sub] as being equal to 1.9*f[sub]ya[/sub], however Hilti appears to take the f[sub]uta[/sub] from the G30.18 rebar standard. Logically this makes sense to do, but I am curious as to why that decision was made when the code does not explicitly indicate to do that. If I were to run this check by hand, I would not be given any instruction to go find this information and would likely just apply 1.9*f[sub]ya[/sub]. Further, Hilti treats R as 0.7, treating rebar as a brittle steel element. In contrast, Simpson Anchor takes R as 0.8; rebar as a ductile steel element.
The inconsistency behind the design calculations is making me wonder if they are just overly conservative. Perhaps someone here has pondered this in the past.