SooryaShrestha
Electrical
- Feb 7, 2001
- 59
I have a 200/1 CT ratio tested with primary injection kit. I have given 100 amp on the primary and got 0.52 amp on the secondary. I have further given 200 amp in the primary and got 1.02 amp in the secondary. Can these values be used to determine the accuracy class of the CT?
I have been informed that since the burden needs to be between 25% to 100% of the rated burden, which is 30 VA, the above values can not determine the accuracy. Is it true?
My third question is: does the accuracy class need to be tested only in the lab? Can the accuracy class be tested in the field? If it can be tested at the field, how sophisticated are the instruments of testing?
I have been informed that since the burden needs to be between 25% to 100% of the rated burden, which is 30 VA, the above values can not determine the accuracy. Is it true?
My third question is: does the accuracy class need to be tested only in the lab? Can the accuracy class be tested in the field? If it can be tested at the field, how sophisticated are the instruments of testing?