sykimk
Electrical
- Dec 28, 2003
- 55
Is it acceptable to use the different CT ratio for Genenerator differential protection?
That is, C400 is used at line side of generator and C800 is used at generator side, and those CTs are used for 87G.
As far as I know, the designation of "C" in ANSI means that it should guarantee 10% of error when 20 times rated primary currents are applied. It is similar to 10P20 (IEC rating).
Therefore, I think it is possible to apply this configuration for generator differential protection when I consider the actual characteristic of CT saturation and short circuts faults outside protective zone during setting of 87G. Furthermore, I think it is not necesary to worry about CT saturation because modern protective relays (digital type) usually require quite small burden.
Could you please advise whether my understanding is correct or not? If I missed anything else, please advise also.
Thanks in advance for your advices.
That is, C400 is used at line side of generator and C800 is used at generator side, and those CTs are used for 87G.
As far as I know, the designation of "C" in ANSI means that it should guarantee 10% of error when 20 times rated primary currents are applied. It is similar to 10P20 (IEC rating).
Therefore, I think it is possible to apply this configuration for generator differential protection when I consider the actual characteristic of CT saturation and short circuts faults outside protective zone during setting of 87G. Furthermore, I think it is not necesary to worry about CT saturation because modern protective relays (digital type) usually require quite small burden.
Could you please advise whether my understanding is correct or not? If I missed anything else, please advise also.
Thanks in advance for your advices.