What are the rules of thumb to choose the CT-ratio of protection CT (O/C and E/F) on a feeder in a substation? I've seen CT's with a low ratio, but the faultlevel on that point is very high.
The faultlevel of our 20MVA, 66/11 kV Trf is approximatly 12kA. The 11kV Incomer have a ratio of 1200/5, 10P10. That seems to be OK. But one of the feeder's CT-ratio's (For a downstream 2MVA 11kV/380V trf) is 120/5, 10P20. Is this ratio correct? I'm a bit confused, because I thought the main aim of protection is to protect against high faultlevels, but I think this feeder's CT's will saturate under a big fault on the primary side of the trf. It seems as if this ratio is been chosen on the faultlevel of a through-going fault on the secondary side of the trf. (Dyn-11 trf, faultlevel 40kA on secondary side, will give 2.4kA on 11kV side) I've seen it on a lot of our substations and it is confusing.
1. On witch faultlevel do you choose the CT-ratio of feeders? ( Faultlevel at that point, or through-going faultlevel of downstream trf)
2.Setting of relay's? ( Also on faultlevel of that point, or on through-going faultlevel of downstream trf)
Any help or sugestions will be appreciated
Regards
Ralph
The faultlevel of our 20MVA, 66/11 kV Trf is approximatly 12kA. The 11kV Incomer have a ratio of 1200/5, 10P10. That seems to be OK. But one of the feeder's CT-ratio's (For a downstream 2MVA 11kV/380V trf) is 120/5, 10P20. Is this ratio correct? I'm a bit confused, because I thought the main aim of protection is to protect against high faultlevels, but I think this feeder's CT's will saturate under a big fault on the primary side of the trf. It seems as if this ratio is been chosen on the faultlevel of a through-going fault on the secondary side of the trf. (Dyn-11 trf, faultlevel 40kA on secondary side, will give 2.4kA on 11kV side) I've seen it on a lot of our substations and it is confusing.
1. On witch faultlevel do you choose the CT-ratio of feeders? ( Faultlevel at that point, or through-going faultlevel of downstream trf)
2.Setting of relay's? ( Also on faultlevel of that point, or on through-going faultlevel of downstream trf)
Any help or sugestions will be appreciated