I have a quick question about current transformers.
I have a relay that requires a CT with a burden of 2.5VA (1A secondary CT) or 7.5VA (5A secondary CT).
I only currently have access to a 400:5 (2.5VA burden) 5P20 CT. However, as my fault and load current is low (less than 80A and 1600A respectively) I was wondering if I could set the relay up as 80:1 and use the 400:5 CT. To my mind this then satisfies the burden and ratio requirements as 80A through my 400:5 CT = 1A and the CT burden is 2.5VA.
Any thoughts welcome.
I have a relay that requires a CT with a burden of 2.5VA (1A secondary CT) or 7.5VA (5A secondary CT).
I only currently have access to a 400:5 (2.5VA burden) 5P20 CT. However, as my fault and load current is low (less than 80A and 1600A respectively) I was wondering if I could set the relay up as 80:1 and use the 400:5 CT. To my mind this then satisfies the burden and ratio requirements as 80A through my 400:5 CT = 1A and the CT burden is 2.5VA.