kaspor
Electrical
- Aug 12, 2021
- 33
Hello
With CT rated burdens, do you need to factor in the resistance of the CT itself into the load burden calculation?
If not, can am I correct with the below calculation?
If we assume the CT is 1000/1A 5P10, assume secondary cable impedance is 0.1ohms, relay burden = 0.1VA
My understanding is in order to gauruntee performance of 5 percent error at 10x rated current (i.e. 10kA), then CT rated burden must be greater than load burden at nominal current (1A).
Total CT burden = Secondary cable burden + Relay burden
Total cable burden = I^2 x Cable Impedance = 1^2 x 0.1^2 = 0.01VA
Relay burden = 0.1VA
Total CT burden = 0.1 + 0.01 = 0.11VA
Hence CT must have a rated burden of >0.11VA? We do not include the burden of the CT itself (i.e. due to CT resistance)?
With CT rated burdens, do you need to factor in the resistance of the CT itself into the load burden calculation?
If not, can am I correct with the below calculation?
If we assume the CT is 1000/1A 5P10, assume secondary cable impedance is 0.1ohms, relay burden = 0.1VA
My understanding is in order to gauruntee performance of 5 percent error at 10x rated current (i.e. 10kA), then CT rated burden must be greater than load burden at nominal current (1A).
Total CT burden = Secondary cable burden + Relay burden
Total cable burden = I^2 x Cable Impedance = 1^2 x 0.1^2 = 0.01VA
Relay burden = 0.1VA
Total CT burden = 0.1 + 0.01 = 0.11VA
Hence CT must have a rated burden of >0.11VA? We do not include the burden of the CT itself (i.e. due to CT resistance)?