Emergency Diesel Generator 1000kVA, 0.38kV, FLA 1519Amps, CT Ratio 2000/5.
As per IEEE C37.102, the pick-up for 51V shall be 150% of the generator FLA. In my case, the 150% of 1519 is 2279Amperes. Now this value is much higher the the CT installed. When I do the setting, I cannot set the pick-up more then 130%.
1. Is it OK to set the pick up at 130% for 51V-R function.
2. My Relay curve for 51V-R is intersecting the Generator Field force curve (although its above the knee of the decrement curve). Is it OK that it is intersection or my Relay curve shall fall to the right of the field force limit.
Thanks