CT Saturation 2

Status
Not open for further replies.

THD

Electrical
May 18, 2002
21
0
0
ZA
We are to comission a system with 1200/1 10p10 CTs. The fault level is 18kA at 11kV. At what point will the CTs saturate? They are connected to Siemens 7SJ protection relays.

Kevin Bosch
Rainbow Technologies
 
Replies continue below

Recommended for you

Ceast-

That is a good paper, but this statement is horribly wrong on many levels:

"Higher ratio cts (3000:5) contribute a resistance of 0.0025 ohms per turn to the burden and lower
ratios (300:5) 0.005 ohms per turn. Consequently, applying a 600 turn (3000:5) ct contributes an
internal resistance of 1.5 ohms."

First, unless the CT is a bushing CT, you can't be sure how many turns are on the secondary. For example, a 230 kV CT with a 300:5A ratio likely has 4 primary turns and 240 turns on the secondary.

Second, there isn't really a good way to give a rule of thumb for ohms/turn based on the ratio. The secondary wire size used is typically a function of the rated secondary current and the rating factor. In other words, the secondary wire is typically the same for the 3000:5A and a 300:5A CT. If anything, lower ratio CTs can often times have larger cross-section cores, which means the lead distance per turn is higher. Also, the diameter of the CT plays a role in secondary resistance, since windings are often equally distributed about the core.

Note sure why such a good paper would be so sloppy with a fairly important parameter.

 