CT Sautration & Pickup

Status
Not open for further replies.

ukgraduate

Electrical
Sep 15, 2011
30
Hi,

I have an application where the prospective fault level is 10kA. The CT ration is 200/1 5P20. So the max current before CT saturates and larger inaccuracies start is around 4kA.

My settings are such that the pickup will occur at 2kA.

Will this CT pose a problem with the high fault level and saturation?
Or is this not an issue because the pickup is below the saturation level?

Regards

UkGrad
 
Replies continue below

Recommended for you

Saturation occurs when the Primary CT current is so High (or above the accuracy rating) that it can not put out a secondary current in a linear fashion. Since your pickup is well below the "Knee" of the saturation curve, You will be fine.

This could cause an issue if say, you have a breaker with C800 CTs and a breaker with C400 CTs and each of these breakers are associated with line and bus protection. If there was a line fault, the C400 CTs could saturate before the C800 cts. The result would be differing secondary currents going to the bus relaying which could cause a false Bus differential trip.
 