When testing bushing CTs on a breaker (3-pole, dead-tank GCBs with 2 CTs per bushing), I've been in the habit of shorting the secondaries of all 12 CTs mounted on the breaker since the burden is isolated and the CTs would be open circuited otherwise. As each CT is tested, I lift the shorting screws from the secondary terminal and connect it to the piece of test equipment.
I've talked to a few people who claim that this is unnecessary and time-consuming during testing and I wanted to get additional input. This does not seem like a good idea to me, but I can't fully explain it for all test sets.
On turns ratio tests, some test sets inject up to 800A of current through the individual poles of the closed breaker by connecting to the bushing terminals on both sides of the pole. If any of the CTs mounted on the phase with the current applied are open circuited, they will build up a dangerous voltage on the secondary. This is no different than an open circuit during normal operation.
Secondary injection test sets explain their turns ratio test as applying a voltage through the secondary and measuring the voltage on the primary by connected leads on the bushings terminals across the pole. The secondary applied voltage can be up to the saturation voltage of the core. I'm having a harder time understanding exactly what's going on with the primary side in this type of test set:
The voltage is dropped across the inductance of the primary bus through the bushing CT, correct? If there are two CTs stacked per bushing, I would think that the flux through the core of the 1st CT could have an effect on the CT directly below or above it. If this nearby CT is open circuited, could it cause issues with high voltages on the secondary? Could the excitation of this core interfere with the readings on the CT being tested?
Thank you.
I've talked to a few people who claim that this is unnecessary and time-consuming during testing and I wanted to get additional input. This does not seem like a good idea to me, but I can't fully explain it for all test sets.
On turns ratio tests, some test sets inject up to 800A of current through the individual poles of the closed breaker by connecting to the bushing terminals on both sides of the pole. If any of the CTs mounted on the phase with the current applied are open circuited, they will build up a dangerous voltage on the secondary. This is no different than an open circuit during normal operation.
Secondary injection test sets explain their turns ratio test as applying a voltage through the secondary and measuring the voltage on the primary by connected leads on the bushings terminals across the pole. The secondary applied voltage can be up to the saturation voltage of the core. I'm having a harder time understanding exactly what's going on with the primary side in this type of test set:
The voltage is dropped across the inductance of the primary bus through the bushing CT, correct? If there are two CTs stacked per bushing, I would think that the flux through the core of the 1st CT could have an effect on the CT directly below or above it. If this nearby CT is open circuited, could it cause issues with high voltages on the secondary? Could the excitation of this core interfere with the readings on the CT being tested?
Thank you.