I was wondering which CT verification formula you are using.
I have to verify the CTs for many substations and I was going to use the formula showed in the attachment.
The "magic" Ktd factor seems to be:
Ktd = 1 for over current relays
Ktd = 1.2 for line differential relays
Ktd = 3 for trasf differential relays
Ktd = 5 for motor or generator differential relays
(I wonder also why CTs for generator differential relays seems to be more critical than the CTs for the transformer differential relays)