Hello all,
I am involved in design of 12.5MVA high resistance grounded (using NGT)hydro plant. Having a discussion on CT sizing on the stators low side. On the high side, bolted fault current is 8574A, which is mostly supplied by the utillity. CT's on the high side C800 600:5 rating.
My question is CT's on the low side of the generator. The low side stator conductors are only going to see generator supplied current and none from the utility. Which means the voltage class rating on these CT's can C100.
I can't see any fault situation where the low side of the stator conductor's, where CT2 is located, would be exposed to anything other than the generator supplied fault current.
I have attached a word doc showing different faults for this scenario.
Thanks in advance for any feedback on this.
RP
I am involved in design of 12.5MVA high resistance grounded (using NGT)hydro plant. Having a discussion on CT sizing on the stators low side. On the high side, bolted fault current is 8574A, which is mostly supplied by the utillity. CT's on the high side C800 600:5 rating.
My question is CT's on the low side of the generator. The low side stator conductors are only going to see generator supplied current and none from the utility. Which means the voltage class rating on these CT's can C100.
I can't see any fault situation where the low side of the stator conductor's, where CT2 is located, would be exposed to anything other than the generator supplied fault current.
I have attached a word doc showing different faults for this scenario.
Thanks in advance for any feedback on this.
RP