Hi,
Need help. We have a 100MVA shunt reactor connected to 400kV bus. Additionally, this shunt reactor has a star connected tertiary that is loaded in emergency conditions.
It's differential protection is misbehaving. Diff protection trips the breaker whenever the breaker is switched (ie. closed). The protection is applied to only across the main winding and uses, thus, the 3 HV post type CT's (Class 10P) and 3 Neutral CT's (internal to SR) (Class X). The protection terminal is latest numeric relay.
Could it be the impact of DC offset on CT's?
Is the application desirable ito different CT classes used?
Thanks.
"Die Here is my Herder..."
Need help. We have a 100MVA shunt reactor connected to 400kV bus. Additionally, this shunt reactor has a star connected tertiary that is loaded in emergency conditions.
It's differential protection is misbehaving. Diff protection trips the breaker whenever the breaker is switched (ie. closed). The protection is applied to only across the main winding and uses, thus, the 3 HV post type CT's (Class 10P) and 3 Neutral CT's (internal to SR) (Class X). The protection terminal is latest numeric relay.