I read the IEEE 519-2002 and the standard have set %THD limits based on Table 11-1 but this is for utility application at the PCC between the industrial plant and utility interconnection (on the metering point).
However, it may be overly conservative if the same limits are applied to the downstream ditribution system. I was warned in the past that IEEE 519-2002 was catered for Utilities not for Industrial Plant downstream distribution (worst case, 20-8Y/120V, 600V, 4.16 kV systems). Assuming no resonance, the % THD is usually greater on where the non-linear loads are connected (mostly on the 600V and 4.16 kV systems in an industrial plant setting).
However, there are tables 10-3 and 10-4 in IEEE 519-2002 which sets the current limits on each harmonic frequency based on Isc/IL ratio and system voltage. Are these tables suitable enough (not overly conservative) to establish harmonic distortion limits for downstream distribution systems in within the Industrial plant power system?
If not or they tend to be overly-conservative, what are good basis for setting limits then for industrial power distribution system?
I read the IEEE 519-2002 and the standard have set %THD limits based on Table 11-1 but this is for utility application at the PCC between the industrial plant and utility interconnection (on the metering point).
However, it may be overly conservative if the same limits are applied to the downstream ditribution system. I was warned in the past that IEEE 519-2002 was catered for Utilities not for Industrial Plant downstream distribution (worst case, 20-8Y/120V, 600V, 4.16 kV systems). Assuming no resonance, the % THD is usually greater on where the non-linear loads are connected (mostly on the 600V and 4.16 kV systems in an industrial plant setting).
However, there are tables 10-3 and 10-4 in IEEE 519-2002 which sets the current limits on each harmonic frequency based on Isc/IL ratio and system voltage. Are these tables suitable enough (not overly conservative) to establish harmonic distortion limits for downstream distribution systems in within the Industrial plant power system?
If not or they tend to be overly-conservative, what are good basis for setting limits then for industrial power distribution system?