proznick
Electrical
- May 26, 2008
- 16
Hello,
I am designing a 10MVA hydro plant. I am using an SEL 387 for current differential. I had designed for shorting test switches between the CT's and the relay but was told that industry standard for the differential relay is not to install shorting test switches but wire the CT through terminal blocks to the relay instead.
I didn't quite see the logic in this as relays are to be tested regularily which would would be easier with the shorting test switches.
Does anyone have any insight into this logic?
cheers
RP
I am designing a 10MVA hydro plant. I am using an SEL 387 for current differential. I had designed for shorting test switches between the CT's and the relay but was told that industry standard for the differential relay is not to install shorting test switches but wire the CT through terminal blocks to the relay instead.
I didn't quite see the logic in this as relays are to be tested regularily which would would be easier with the shorting test switches.
Does anyone have any insight into this logic?
cheers
RP