People,
Can someone explain the mathematics behind the current that flows in one of the legs of a motor in star delta configuration. There are six connections - one from each end of the six coil terminals.

I believe that if the motor full load current is 100%, then the current magnitude in each leg is 58% (=1/sq root of 3).

Much Thanks
 
Replies continue below

Recommended for you

Adding to previous post:
There are three circuits in the motor. Phase A is T1 and T4. Phase B is T2 and T5. Phase C is T3 and T6. The motor you have may have different markings such as U1-U2, V1-V2, W1-W2. Same thing. When the motor is connected star, or wye, the voltage that is applied to the winding is 1/1.732 times phase voltage. When the connection is changed to delta then phase voltage is line voltage.
If you have a nameplate rated 460 volt motor rated star start and delta run then the motor will be connected for 796 volts on start but will only get 460 volts applied; so it starts a little slower. When the contactors connect it to delta then the motor attains full power. Acceleration time is dependent on the load. Hope this helps.
 
Yes, the current in each of six leads is 0.577 per-unit of nameplate. Remember to apply (99)NEC310-15(b)(2)(a) ampacity-adjustment factors if the six leads are in a raceway or cable.
 