- Oct 15, 2001
- 2
I intend to use a 4,000A current limiting fuse to be installed right after the load terminals of a power CB with a 75kAIC rating in an existing switchboard (there is no space available to install the CLF at the line terminals of the breaker). Will the CLF protect the breaker for a 110kA symmetrical RMS available fault current considering the let-through of this fuse is between 57 to 65 kA (depending on the brand and type of fuse; based on the let-through curve)? Based on my understanding on the operation of the CLF, the CLF will not allow a current higher than this level, i.e. 57 or 65kA. and thus protecting the breaker. The CLF will be installed right after the breaker where the possibility of a fault between the breaker and fuse is almost nil.