tem1234
Electrical
- Jun 13, 2007
- 192
Hi guys,
Attached is the one line of the situation.
All the 600 V breaker are rated 42 kA, and the calculated Short circuit current is 50-55 kA approximately.
I am wondering if it is a good solution (economically and practically) to add current limiting reactor to limit the short-circuit current under 42 kA.
There's 3 place I see where i can put the reactor:
- at 600 V (location 3), but the nominal current of the reactor should be 4000 A, so i don't know if it's a good way. Also, maybe more expensive compare to replace the breaker.
- at 6.9 kV (location 1 or 2). At location 1, I only need 3 reactor (1 per phase) instead of 9, but the nominal current will be 1200 A instead of 400 A (or less, the transformer aren’t full load).
Maybe there will be a voltage drop at full load on the reactor, but we can change the tap on the transformer to adjust the voltage at full load.
Do you have any experience with current limiting reactor and it is a good way to solve this problem. Changing all the breaker will cost a lot of money, but maybe add reactor will be expensive too. What do you think of this?
Thanks
Attached is the one line of the situation.
All the 600 V breaker are rated 42 kA, and the calculated Short circuit current is 50-55 kA approximately.
I am wondering if it is a good solution (economically and practically) to add current limiting reactor to limit the short-circuit current under 42 kA.
There's 3 place I see where i can put the reactor:
- at 600 V (location 3), but the nominal current of the reactor should be 4000 A, so i don't know if it's a good way. Also, maybe more expensive compare to replace the breaker.
- at 6.9 kV (location 1 or 2). At location 1, I only need 3 reactor (1 per phase) instead of 9, but the nominal current will be 1200 A instead of 400 A (or less, the transformer aren’t full load).
Maybe there will be a voltage drop at full load on the reactor, but we can change the tap on the transformer to adjust the voltage at full load.
Do you have any experience with current limiting reactor and it is a good way to solve this problem. Changing all the breaker will cost a lot of money, but maybe add reactor will be expensive too. What do you think of this?
Thanks