Tek-Tips is the largest IT community on the Internet today!

Members share and learn making Tek-Tips Forums the best source of peer-reviewed technical information on the Internet!

  • Congratulations cowski on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Current Measurement Device

Status
Not open for further replies.

AdamAReid

Electrical
Joined
Sep 17, 2002
Messages
5
Location
CA
Hello,

I am looking for two current measuring devices. They both need to be remote (non-handheld), and send out a signal (such as analoge voltage) that can be interpreted by a data logger, for transmission into a PC.

The first needs to measure the current being drawn by a 24V DC Motor (drawing between 0-7amps).

The second needs to measure the current being drawn by a 5.5kW AC Motor (0-14amps).

I was thinking about some kind of current shunt module.
Any ideas (or recommend some informative websites?). I've heard of sensors that "wrap" around the supply cable and read current. Would such sensors be more appropriate?
Thanks,
AAR
 
Thanks Lewish,

By remote, I mean it needs to be stand-alone... I can't be there to hold it or position it. It needs to be something (non-hand held) that I can affix to a cable to read the current going through it, and, it needs to send out a signal that a simple datalogger can read (like, say, voltage increase with current increase) and send to a PC.
Looking for something small and cost-effective.

Thanks agian for your advice,
AAR
 
There are many options but to keep it low cost try Load Controls Inc (True rms measuring) or if TRMS is not a concern then go with someone like SSAC, Diversified Electronics, or Veris Industries. Good luck.
 
Both the measurements can be done using a current transformer. The ac signal can be measured using a wired-in transformer or a "split core transformer" if you don't want to disconnecet the circuit. You can also get a "DC"current transformer (this is a form of dc-dc converter) for the DC signal. Most electronic vendors such as Maplin or Electrosonic sell these. You might use a shunt for the DC signal but this depends upon the earthing arrangements and in any case its not a bad idea to use transformers to isolate your supplies from the PC. If you use a current transformer do remember to always terminate the secondary in some resistance for safety reasons.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top