Current Transformer - Imag Specifation

Status
Not open for further replies.

YERUK123

Electrical
Feb 5, 2012
15

Why is that Magnetizing current ( Imag ) measured or Specified mostly at Vk /2 (Vk= Knee point Voltage ) in the Current Transformer discription ?
 
Replies continue below

Recommended for you

Guys Any response for the above question ?
 
Which Current Transformer description are you referring to? Some standard?

A bit more info is needed.
 
Normally if a Iexc (excitation current) limit is specified it is specified at Vkp (knee-point voltage).

I've seen Iexc limited at Vkp/2, but it's very rare. My assumption when that was specified was that someone was trying to spec a CT to match exactly to an existing unit and took it to another level above Iexc @ Vkp.


 
@ Vertias : Class of CT is PX or X , Standard is IEC
@ Scottf : Some manufcaturer specify it Imag ( magnetising Current ) at Vk (Knee Point Voltage ) and Few at Vk/2 . But These are for new substations and not matching any other existing CT
 
The IEC 60044.1 standard says Ie is the maximum exciting current at the rated knee point emf and/or at a stated % thereof.

I have never seen it yet specified at a fraction of Vk but the standard allows for it. The reason why Ie is specified in this way is to ensure matched characteristics at Vk for a group of CT's used for a differential application. Matched characteristics minimises the spill current due to CT mismatches. In other words, it is intended to ensure superior performance than say if a Class P CT was used for the same application.

Alternatively stated the B-H characteristic passes through the same point for the matched CT's.
 