electricpete,
In this case you would want to take into account the power supply internal resistance since the CT resistance will be as low or lower than the power supply resistance throwing off the final result.
.... this is just a POSSIBLE way of doing CT measurement, it gets you into the ballpark .... there are errors that would need to be considered, as you mentioned lead length, etc ..... but Elhouni is out in the field ... without lab equipment ... if I want the most accurate I would definetely use the 4-wire method you described ....
... another possible way would be to use a DUCTOR ... but it can be a real pain holding down the contact points until you get a stable reading .... and you can only get a DC reading at that ....
.... but these are issues of accuracy that only Elhouni can answer .... how critical is the accuracy? Are ballpark values good enough for his calculations?
as for the the application ... to quote "this value of the secondary winding resistance will be used for the calculations of CT performance against saturation" ... the response by 230842 on Dec, 10 pretty much nailed that one ...
which brings it back to accuracy ..... how accurate does he want his calculation?
... or maybe I am already out in left field .....