lanejoe10
Structural
- May 13, 2010
- 10
IBC section 2403.3 limits the deflection perpendicular to an individual glass lite to l/175 or 3/4" whichever is less.
I have a 35ft tall mullion, the first like is 15ft tall, the 2nd lite is 8ft tall and the 3rd lite makes up the remainder. I will limit my mullion deflection to l/240+1/4".
How do i check the deflection of the 1st lite to make sure it meets IBC section 2403.3? Seems that the 1st lite is almost a cantilever beam, so would I want to limit the deflection at 15ft to 2*15ft/175 or 2*3/4"?
If anyone can shed any lite (light) on this, that would be greatly appreciated.
Also, AAMA TIR-A11-15 states:
"The 19 mm (3/4 in) framing deflection limitation is then only appropriate for single lite high applications. For members supporting multiple lites, a 19 mm (3/4 in) limit places unwarranted demands on taller framing systems which may result in increased sitelines (framing widths), depths or reinforcing requirements."
This almost seems like the requirement doesn't apply to mullions that are supporting multiple lites like I have.
I have a 35ft tall mullion, the first like is 15ft tall, the 2nd lite is 8ft tall and the 3rd lite makes up the remainder. I will limit my mullion deflection to l/240+1/4".
How do i check the deflection of the 1st lite to make sure it meets IBC section 2403.3? Seems that the 1st lite is almost a cantilever beam, so would I want to limit the deflection at 15ft to 2*15ft/175 or 2*3/4"?
If anyone can shed any lite (light) on this, that would be greatly appreciated.
Also, AAMA TIR-A11-15 states:
"The 19 mm (3/4 in) framing deflection limitation is then only appropriate for single lite high applications. For members supporting multiple lites, a 19 mm (3/4 in) limit places unwarranted demands on taller framing systems which may result in increased sitelines (framing widths), depths or reinforcing requirements."
This almost seems like the requirement doesn't apply to mullions that are supporting multiple lites like I have.